【常见问题】吸水管与母管、吸水管与水泵进水口未采用管顶平接

发布于:2024-11-08 14:38

【问题描述】吸水管与母管、吸水管与水泵进水口未采用管顶平接

 

《 消防给水及消火栓系统技术规范》 GB50974-2014

5.1.13 离心式消防水泵吸水管、出水管和阀门等,应符合下列规定:

    2 消防水泵吸水管布置应避免形成气囊;

 

12.3.2 消防水泵的安装应符合下列要求:

    7 吸水管水平管段上不应有气囊和漏气现象。变径连接时,应采用偏心异径管件并应采用管顶平接

 

来源:青岛市建设工程消防验收给排水专业常见问题(2024版)