排烟风管能否穿越防烟楼梯间

排烟风管能否穿越防烟楼梯间,因为现场情况特殊,消防排烟风管太大,影响吊顶空间,采取防火包裹两端加防火阀,

是否能穿越防烟楼梯间?,大约2米长度。

消防网友65069 | 2025-03-30 16:22
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

EHS专家-DL 2025-03-31 09:14 10 [回复]举报

  1. 一般禁止性要求
    防烟楼梯间作为核心疏散通道,其防烟完整性需严格保护,原则上不允许排烟风管直接穿越‌。若普通风管穿越会形成额外孔洞,可能违反《高规》关于防烟楼梯间内墙禁止开设非必要洞口的规定‌。

  2. 特殊情况的许可条件
    当现场条件受限且无法避免时,需满足以下强制性技术措施:

    • 穿越段风管应采用‌耐火极限≥2.0h的防火包裹‌,且不得影响人员疏散‌。(穿越长度≤2米时,需确保风管‌不占用疏散通道有效宽度‌,且与周边墙体保持≥200mm防火隔离间隙‌
      )
    • 风管两端需设置‌70℃防火阀‌(排烟系统专用防火阀)‌。
    • 穿越区域应设置‌独立防火分隔构造‌(如土建夹层或耐火板封闭空间)‌
    • 禁止在楼梯间内设置风管‌检修口或连接件‌,避免破坏防烟性能‌。
    • 合规性确认流程

      • 提交穿越方案至当地消防部门进行‌专项审批‌,并提供防火包裹材料检测报告、防火阀产品认证文件等支撑材料‌。
      • 建议委托第三方消防检测机构对穿越段进行‌耐火极限实测验证‌‌。

wetom 2025-03-31 09:18 10 [回复]举报

确有困难必须从楼梯间穿过,那就考虑防护措施,这种非标问题,这里是不会有答案的,每个人的理解都不一样,直接咨询具体负责验收的建筑专家吧

shijieyang40 2025-04-01 09:01 00 [回复]举报

参考浙江省的标准:除加压送风管道外,通风(空调)风管、排烟管道不应穿越建筑内楼梯间、前室(含建筑首层由走道和门厅等形成的扩大封闭楼梯间、防烟楼梯间扩大前室)、避难区及避难走道等防烟部位。当受条件限制必须穿越时,通风(空调)风管、排烟管道应采用耐火极限不低于 2.00h 的隔墙和 1.50h 的楼板进行防火分隔。对于避难区(间)等场所,当采用楼板进行防火分隔确有困难时,穿越避难区(间)的风管应采用耐火极限不低于 2.00h 的防火风管,或采用耐火极限不低于 1.00h 的防火风管,且采用耐火极限不低于 1.00h 的防火吊顶进行防火分隔。