消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

气体灭火系统机械应急启动

气体灭火系统机械应急启动

1.直接开储瓶剂上的瓶头阀 通过储瓶里的气体开后续瓶头阀,直接动作喷放是否正确?

2.根据顺序开驱动气体,开选择阀开出储瓶剂瓶头阀,直接喷放,是否正确?

空中 | 2025-04-22 18:29
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

小唐12321 2025-04-23 08:11 00 [回复]举报

有没有选择阀,一般直接开启驱动气瓶,看工作原理

EHS专家-DL 2025-04-23 09:37 00 [回复]举报

‌问题1:不完全正确。机械应急启动的核心操作并非直接手动开启灭火剂储瓶的瓶头阀,而是通过操作驱动气体瓶组释放启动气体,间接打开灭火剂储瓶的瓶头阀。具体流程如下: 1、在控制器失效时,需先关闭联动设备并切断电源,随后打开对应防护区的选择阀。2、通过驱动气体瓶组上的机械装置(如拔除安全插销、压下圆头把手等),释放启动气体,利用驱动气体压力依次开启选择阀和灭火剂储瓶的瓶头阀。 因此,直接开启储瓶剂瓶头阀不符合标准操作流程,可能导致气体未通过选择阀定向释放,影响灭火效果。

问题2:正确。机械应急启动必须严格遵循“驱动气体→选择阀→储瓶剂瓶头阀”的顺序,以确保灭火剂正确释放。

空中   回复: EHS专家-DL2025-04-23 10:08

那请问,如果驱动气瓶无法动作,此时方法一是否可行

0    0 [回复]举报

EHS专家-DL   回复: 空中2025-04-23 12:03

少数特殊设计的系统(如无驱动气体瓶组的简化装置)可能允许直接手动开启灭火剂瓶头阀,但需明确产品说明书支持此类操作。一般组合分配系统必须通过驱动气体开启选择阀,否则可能导致多防护区误喷。

0    0 [回复]举报

小唐12321   回复: 空中2025-04-23 14:37

如果是很多个怎么一起开启,开启时间不能太长,后面是不是有选择阀,又怎么开启

0    0 [回复]举报

空中   回复: 小唐123212025-04-23 17:39

我想问的是:

只靠储气瓶压力是否能满足开启相对应的选择阀  启动系统

如果不能 在驱动气瓶失效时 

系统该如何启动

0    0 [回复]举报

消防资源网   回复: 空中2025-04-24 09:18

不能,只能一个一个去启动

0    0 [回复]举报

牛丫头消防课堂   回复: 空中2025-05-01 18:30

机械应急操作的正确顺序是,先打开对应的选择阀,再拔下驱动气瓶电磁阀的安全销,拍下,电磁阀动作,驱动气体去打开灭火剂瓶,如果驱动气瓶压力满足,就可以打开灭火剂瓶头阀,但是如果驱动气瓶压力不足,就需要人工操作灭火剂气瓶的瓶头阀;所以不管咋说,必须先打开选择阀,如果不打开选择阀,气体无法通往防护区。

1    0 [回复]举报

消防资源网 2025-04-24 09:27 00 [回复]举报

不能,只能一个一个手动去启动

关闭

关闭

手机APP下载