消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

工业建筑室内消火栓直接接入市政管网,水压不够0.35MPa?

有一些单层的工业建筑,没有设立消火栓泵,室内消火栓直接接入市政管网,由市政管网提供水压,压力一般只有0.2左右。

而规范规定的工业建筑室内消火栓动压要求0.35MPa。

现实中这些建筑水压达不到0.35MPa,合规吗?

还是有其他合理的解释,而我不知道的?

牧阳人 | 2021-08-02 10:33
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

刘丽波 2021-08-04 08:39 00 [回复]举报

市政的消防水压无法满足要求时,如果市政允许消防泵直接吸水可以只设加压泵;如不允许,需要设置消防水池➕ 消防泵。

消防网友68347 2023-12-26 16:02 00 [回复]举报

室内消火栓动压0.35,实验消火栓处也需要满足吗?

关闭

关闭

手机APP下载