消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

爆炸危险区划分问题

依据《爆规》GB50058,一个房间内定性为1区,房间外门洞XXm范围为2区,如果室内室外都满足通风良好条件,是不是房间内就可以划分为2区,室外就全部是安全区了?可是规范并没有说明2区能够降为安全区呢

chowah | 2022-12-09 11:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

石小东 2022-12-09 16:43 10 [回复]举报

 爆炸危险环境电力装置设计规范 GB50058-2014 ,3.2.4 当爆炸危险区域内通风的空气流量能使可燃物质很快稀释到爆炸下限值的25%以下时,可定为通风良好,并应符合下列规定:
    1 下列场所可定为通风良好场所:
        1)露天场所;
        2)敞开式建筑物,在建筑物的壁、屋顶开口,其尺寸和位置保证建筑物内部通风效果等效于露天场所;
        3)非敞开建筑物,建有永久性的开口,使其具有自然通风的条件;
        4)对于封闭区域,每平方米地板面积每分钟至少提供0.3m3的空气或至少1h换气6次。
    2 当采用机械通风时,下列情况可不计机械通风故障的影响:
        1)封闭式或半封闭式的建筑物设置备用的独立通风系统;
        2)当通风设备发生故障时,设置自动报警或停止工艺流程等确保能阻止可燃物质释放的预防措施,或使设备断电的预防措施。
3.2.5 爆炸危险区域的划分应按释放源级别和通风条件确定,存在连续级释放源的区域可划为0区,存在一级释放源的区域可划为1区,存在二级释放源的区域可划为2区,并应根据通风条件按下列规定调整区域划分:
    1 当通风良好时,可降低爆炸危险区域等级;当通风不良时,应提高爆炸危险区域等级。
    2 局部机械通风在降低爆炸性气体混合物浓度方面比自然通风和一般机械通风更为有效时,可采用局部机械通风降低爆炸危险区域等级。
    3 在障碍物、凹坑和死角处,应局部提高爆炸危险区域等级。
    4 利用堤或墙等障碍物,限制比空气重的爆炸性气体混合物的扩散,可缩小爆炸危险区域的范围。

这部规范中有明确的规定

关闭

关闭

手机APP下载