消火栓的进水方式

验收一个办公楼,他的室内消火栓是上进水的。我感觉不对,但是找不到标准。有具体的规范要求不允许上进水吗(就是消火栓进水管在消防箱上侧,消火栓是倒着安装的)

| 2023-04-05 07:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

张牙舞爪的张 2023-04-05 22:10 10 [回复]举报

消火栓口安装可以与墙面垂直向下或平行安装;当室内消防管网不是环状,地下车库消火栓就是描述的那种安装方式。

消防老胡 2023-04-08 20:40 10 [回复]举报

因为大多数室内消火栓水平干管管径基本上是DN100或DN150的,采用预制三通或机械三通与DN65立管连接。如果上进水,DN65管无法在其最低处(箱体内部栓口处)给予其可靠的水平支撑(要使栓口水平或向下都很难实现),带压带栓头的管网容易脱落。

猫儿哥哥 2023-04-09 16:22 10 [回复]举报

国标图集及规范并没有对这个上进水还是下进水有具体要求,原则就是,只要消火栓满足压力要求,高度满足规范要求,系统正常使用,就可以视为合格