消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

变配电室通风排烟问题

公司一个新环保项目配套了高低压配电室,消防方面关于这个配电室要排烟设施吗?

远古鱼龙 | 2023-04-14 11:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

消防老胡 2023-04-14 12:02 10 [回复]举报

       因不清楚这个项目是否属于工业项目还是民用配套环保,根据《工业建筑供暖通风与空气调节设计规范》( GB50019-2015)第6.1.18条:建筑物的防烟、排烟设计应按现行国家标准《建筑设计防火规范》GB 50016的有关规定执行。而《建筑设计防火规范 》(GB50016-2014(2018年版))第8.5.3条:民用建筑的下列场所或部位应设置排烟设施:…… 4 公共建筑内建筑面积大于300m²且可燃物较多的地上房间”和第 8.5.4条“地下或半地下建筑(室)、地上建筑内的无窗房间,当总建筑面积大于200m²或一个房间建筑面积大于50m²,且经常有人停留或可燃物较多时,应设置排烟设施”。故只要符合《建规》2款规定的都要上排烟系统。

       值得注意的是:如果该设备用房设置了例如七氟丙烷等气体灭火系统的,还有配套设置事故排风系统。这个与排烟系统是二回事,可以合用,但必须经厂家深化设计。

      根据《民用建筑电气设计标准》,有的设备用房还需要设置通风设施。

       综上。涉及了3个关于送排风的类别。

远古鱼龙   回复: 消防老胡2023-04-14 16:52

谢谢你的答复,这是个炉头烟治理项目属于工业构筑物,配电室不大不小,没有机械通风设施。有对配电室这块专业很熟的就好了,我感觉配电室不说四要上抽排烟系统,至少要有个轴流风机吧

0    0 [回复]举报

远古鱼龙 2023-04-14 16:55 00 [回复]举报

请问有配电工程熟悉的或是专业的大神吗?

286914067@qq.com 2023-04-15 13:58 10 [回复]举报

高低压配电室,需做气体灭火,需要做事故通风,不是做排烟设施吧!

远古鱼龙   回复: 286914067@qq.com2023-04-17 13:16

对就是事故通风,我看配电室都有轴流风扇!是不是那个规定里有要求?

0    0 [回复]举报

关闭

关闭

手机APP下载