消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

若采用自然补风,相邻两个防烟分区直接从室外引入空气是什么意思,比如库房和营业区为两个防烟分区,补风口直接采用营业区直通室外的门进行补风,库房无直通室外的门,那么库房和营业厅可以都通过营业厅的外门进行补风吗

通用新规及旧规“除地上建筑的走道或地上建筑面积小于500m²的房间外,设置排烟系统的场所应能直接从室外引入空气补风,且补风量和补风口的风速应满足排烟系统有效排烟的要求”,都提到补风应能直接从室外引入空气进行补风,


比如库房和营业区为两个防烟分区,补风口直接采用营业区直通室外的门进行补风,库房无直通室外的门,那么库房和营业厅可以都通过营业厅的外门进行补风吗,换个说法就是库房通过营业厅的补风口补风,算直接从室外引入空气吗

库房和营业区之间是防火隔墙和甲级防火门

南山桂花 | 2023-06-29 09:49
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2023-06-29 11:15 00 [回复]举报

不可以

whale 2023-06-30 10:00 00 [回复]举报

不可以,库房和营业区之间是防火隔墙和甲级防火门”,那库房和营业厅就不是同一个防火分区。

如果是同一防火分区内的两个不同防烟分区则可以共用营业厅的外门进行补风,库房和营业区之间墙体开洞或者百叶,保证两个防烟分区连通。

南山桂花   回复: whale2023-09-15 11:01

这个应该不行,因为商场内的库房墙体按照人员密集场所规范,要求耐火3小时,开洞或者百叶我感觉是破坏了墙体的耐火性

0    0 [回复]举报

潘天坤 2024-07-03 12:28 10 [回复]举报

防火门不能作为补风口

普通门一般也得作联动开启之类的,还不一定被认可

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑


关闭

关闭

手机APP下载