消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

车库内的人防分区,可以不设排烟风口,利用人防分区外的排烟风口排烟吗?

同一个防火分区内的,人防分区内不设排烟风口,仅利用分区外的车库排烟风口,进行排烟,当做同一个防烟分区。人防分区及非人防分区总面积不超2000平方米。是否可行?

飞云 | 2023-07-11 17:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

whale 2023-07-12 11:12 00 [回复]举报

可以,需要保证人防区和给人防区在储烟仓以内联通面积满足要求。

我们这边要求防烟分区不宜跨越人防防护单元,当必须跨越时,人防门下净高与清晰高度之间的高差乘以人防门宽度,这个联通的截面积,按3万多全排烟量,截面积风速不大于10米。

关闭

关闭

手机APP下载