消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

这是湿式报警阀吗?

你好,这是湿式吗?上下两个阀为什么都长关

珊珊呀 | 2023-08-24 20:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

寒江孤影 2023-08-25 10:19 00 [回复]举报

看着像湿式报警阀,报警阀一般情况下,只有进出水两个信号阀和通往报警管路的球阀是保持常开状态的,其他的试水阀、旁通阀等都是关闭状态的

罗文斌 2023-08-29 09:50 00 [回复]举报

应该是湿式报警阀,上面的阀门是泄水阀(实验阀)应是常关(打开后会有有压水排出,等待5分钟以内警铃,压力开关会动作,水泵启动),下边这个阀门是报警管路阀门,应为常开(打开后正常不会排水,喷淋末端或者上面泄水阀打开以及水泵启动时会有水排出,并且警铃动作),如果下面的阀门关闭那么消控室将会收不到这个报警阀组的报警信息。题外话,这个报警阀组看起来比较老,建议和物业人员在场的情况下在开阀门,也有可能报警阀组故障这个阀门不能开

关闭

关闭

手机APP下载