消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

上下喷采用DN25管,是否与规范冲突

今天检查一家二装验收,上下管道及配水管均采用DN25管道,安装方式为4通管道,上下2个喷头,左侧接一根DN25管道穿过墙面,另一面喷头用堵头封堵,4通另一侧接配水管道,我方提出规范规定DN25管道只能接一只喷头,被检查方说上下算一个计算,配水管道可以使用DN25带2个喷头,此项有争议,不予签字。请教下大神们对此看法,因为问了好几个一消同行,有说可以也有说不可以

消防网友67773 | 2024-01-18 15:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

WeiHL 2024-01-18 16:57 10 [回复]举报

上下喷头又不会同时喷水,当然算一个

南明离火 2024-01-19 08:57 00 [回复]举报

上下只算一侧

消防网友62117 2024-01-19 16:24 00 [回复]举报

上下侧均不应超8只,意味者只要算喷淋多的一侧不超8个就行,《喷规》6.2.3条在计算报警阀点位时也只算多的一侧喷淋头可以佐证

关闭

关闭

手机APP下载