消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

储油间与柴油发电机房的防火门

储油间与柴油发电机房的防火门是否采用甲级防火门

滴水石穿 | 2024-04-15 10:43
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

南明离火 2024-04-16 08:47 00 [回复]举报

5.4.13 布置在民用建筑内的柴油发电机房应符合下列规定:
    1 宜布置在首层或地下一、二层。
    2 不应布置在人员密集场所的上一层、下一层或贴邻。
    3 应采用耐火极限不低于2.00h的防火隔墙和1.50h的不燃性楼板与其他部位分隔,门应采用甲级防火门。
    4 机房内设置储油间时,其总储存量不应大于1m³,储油间应采用耐火极限不低于3.00h的防火隔墙与发电机间分隔;确需在防火隔墙上开门时,应设置甲级防火门。
    5 应设置火灾报警装置。
    6 应设置与柴油发电机容量和建筑规模相适应的灭火设施,当建筑内其他部位设置自动喷水灭火系统时,机房内应设置自动喷水灭火系统。

消防网友11625   回复: 南明离火2024-04-26 07:20

你还可以用这个规范的网站吗?


0    0 [回复]举报

南明离火   回复: 消防网友116252024-04-26 11:54

可以啊 你不是也在这边留言提问

0    0 [回复]举报

后格风法 2024-04-16 09:00 00 [回复]举报

应采用。建筑防火通用规范4.1.5储油间应采用耐火极限不低于3.00h的防火隔墙与发电机间、锅炉间分隔。墙体已经需要满足耐火极限3个小时,所开的门同样需满足要求。

关闭

关闭

手机APP下载