消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于消防救援口设置高度的要求是否取消

建规要求消防救援窗设置高度不宜大于1.2m,而建筑防火通用规范改为救援口后对窗户高度未做要求,在实际执行中是否按照建规要求执行?

ruihua | 2024-04-26 09:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

小凡007 2024-04-26 11:54 10 [回复]举报

未提到还按建规执行

安洪全 2024-04-26 13:29 20 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版)中的7.2.5没有被通用规范废止,之前也不是强条。


所以还是参照建规执行即可。



@李帅 2024-04-26 14:18 00 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版)

7.2.5 供消防救援人员进入的窗口的净高度和净宽度均不应小于1.0m,下沿距室内地面不宜大于1.2m,间距不宜大于20m且每个防火分区不应少于2个,设置位置应与消防车登高操作场地相对应。窗口的玻璃应易于破碎,并应设置可在室外易于识别的明显标志。

个人意见:建筑防火通用规范 未体现的,还需要按照 建筑设计防火规范 执行。

13825468008 2024-04-26 14:30 00 [回复]举报

我觉得应该两本规范结合着来,高度应该不小于1.2米。且条文说明也说了,超过1.2米,对消防员进出是不方便,也不安全的。

南明离火 2024-04-26 15:42 00 [回复]举报

通用规范全文强制条文,建规中本身救援窗高度<1.2m就是非强制条文,所以无需体现,仍按建规要求施行

关闭

关闭

手机APP下载