消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水池设置问题

各位老师,关于设置水池的这条规范,我不是很理解,以下:

(1)这条规范我理解是针对室内外所有消防给水设施设置水池的,比如室外消火栓,室内消火栓,市内喷淋,不知是否正确;

(2)其中第2条,只说了室外设计流量大于20L/s这个条件,是不是理解成不管室内用设计流量如何,只按照这个室外20L/S考虑,小于这个就可以单路供水?

秃头哥 | 2024-11-12 07:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

jinyanwu 2024-11-12 15:03 00 [回复]举报

第一条就是市政供应消防和生活共用,如果生活用水太多,市政不能满足要求(不管单路还是双路管道),那么需要设置消防水池;

第二条的意思是如果单路供水,并且室外栓流量大于20(这里不管室内流量,只要单路供水并且室外大于20),那么需要设置消防水池;

第三个和第一条意思应该类似;市政仅供消防使用并且流量不足的情况下,不管单路或者双路;

秃头哥   回复: jinyanwu2024-11-12 17:08

感谢前辈,第一次提问,得到回复很感激,对于第二条还是有点困惑,我是否可以这样理解,单路供水,如果室外栓设计流量小于20,那么我就不用设置水池,此时室内消防用水,直接设置水泵从市政给水吸水就行把

0    0 [回复]举报

jinyanwu   回复: 秃头哥2024-11-13 08:42

其实第二条应该和第三条放到一起就好理解了,就是说如果市政水同时也满足室外+室内栓流量要求,那么单路供水,且室外流量小于20可以不设置消防水池。

例如:市政水流量50,室外15,室内30,那么单路供水可以不设置消防水池(符合第二条款);

这样说:如果单路供水,虽然室外栓流量小于20,但是市政栓供水流量不能满足室内外流量需要时,需要设置消防水池;

例如:市政水流量50,室外15,室内40,单路(包括双路)供水需要设置消防水池,因为不够用(符合第一和第三条款);

          市政流量50,室外25,室内15,单路,供水够用也不行,需要设置(符合第二条款);

          市政流量50,室外25,室内30,需要设置(符合第一和第三条款);

第三条就相当于补充条款;

对于规范来说,你要把条款里面所有情况综合到一起去看,甚至包括其他规范相关条款,不是仅仅只看其中一条就判断是否符合或是否需要,而是三条同时看;

做设计时,就要把这三个条件都计算一下;只要其中一个条件需要设置,那就设置。

0    0 [回复]举报

秃头哥   回复: jinyanwu2024-11-17 14:37

回答太细致了,感谢前辈

0    0 [回复]举报

秃头哥   回复: jinyanwu2024-11-17 14:46

其实我的理解一直有个误区,规范说的是满足其中之一就要设置水池,这是“或”的关系,但是要想不设水池,那这三条就是“与”的关系,所以一直没整明白,语文没学好。

0    0 [回复]举报

消防网友68723 2024-11-13 09:21 00 [回复]举报

且室外栓流量大于20,说明建筑体量大或火灾危险性高,所需消防用水量大,但只有一路消防供水或一条入户引入管,当然需设消防水池

关闭

关闭

手机APP下载