防排烟风管连接方式 必须角钢连接法吗?






上图风管连接:薄钢板连体法兰 现在给用?不应该用角钢连接+螺栓固定吗?

请指出上图 风管连接的毛病和正确的方式 









知耻也要问 | 2025-05-20 15:36
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

牛丫头消防课堂 2025-05-20 22:36 10 [回复]举报

错误:你现在是采用共板法兰咬口连接,不符合要求,应采用角钢法兰连接,或采用共板法兰螺栓连接

知耻也要问   回复: 牛丫头消防课堂2025-05-27 17:45

多谢,抖音也关注你了

1    0 [回复]举报

潘天坤 2025-05-21 08:17 10 [回复]举报

近期设计的项目的防排烟管道,应采用螺栓连接(矩形风管法兰四角应设有螺孔,薄钢板法兰风管应采用螺栓连接,同时还有螺栓孔的间距要求),就是应按楼主所说的螺栓固定,至于是否用角钢的话规范没有限定,从连接固定方式来说满足法兰四角应设有螺孔、采用螺栓连接及螺栓孔的间距要求即可



薄钢板法兰矩形风管(共板法兰矩形风管)不得用于高压风管(工作压力大于1500Pa),从国家技术标准来说没有禁止其他系统(非高压系统)的风管采用薄钢板法兰风管(共板法兰风管)


《薄钢板法兰风管制作与安装》07K133图集上有提到:对于风管边长尺寸大于2000毫米的风管应采用角钢或其他形式的法兰风管(虽然本图集已经说明不适用于圆形风管和防排烟风管,并且图集不是规范,可以参照此尺寸要求)


同时薄钢板法兰风管(共板法兰风管)用于防排烟系统中有一些要求:壁厚(按高压要求执行)、连接方式(矩形风管法兰四角应设有螺孔,薄钢板法兰风管应采用螺栓连接)、法兰高度(用于中压及以下压力系统风管的薄钢板法兰矩形风管的法兰高度,应大于或等于相同金属法兰风管的法兰高度)、风管法兰连接垫片厚度(不应小于3毫米)、风管燃烧性能(有耐火极限要求的本体、框架与固定材料、密封垫料等必须为不燃材料)、螺栓孔距(高压系统不得大于100毫米,其他系统不得大于150毫米)、安装工艺(绝热材料施工、风管加固及弯管导流片的设置等)、强度及严密性(强度及允许漏风量应符合要求)


最后就是《薄钢板法兰风管制作与安装》07K133图集提到:本图集不适用于圆形风管和排烟风管,排烟系统若采用薄钢板法兰风管(共板法兰风管)时不应参照此图集,工作压力不大于1500Pa且边长小于2000毫米的防烟系统(机械加压送风系统)风管可以参照《薄钢板法兰风管制作与安装》07K133图集安装,要特别说明:圆形风管和排烟风管只是不适用于本图集,不能用适用性推导排烟不能采用薄钢板法兰矩形风管(共板法兰矩形风管),这是一个错误的推导