公司仅设置了区域报警系统的,需要按24小时值班,每班不少于2人的标准值班嘛?值班人员需要取得消防设施操作员证嘛?如果需要,具体的标准规范麻烦专家提供一下,谢谢!

石小东 | 2022-03-19 17:31
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

五棱镜中看世界 2022-03-21 15:04 00 [回复]举报

在区域报警系统里,可以根据需要不设消防控制室,若有消防控制室,火灾报警控制器应设置在消防控制室;若没有消防控制室,则应设置在平时有专人值班的房间或场所。设置消防控制室则需3班每班2人进行24h值班,人员需取得建构筑物消防员资格证:建筑消防设施的维护管理 GB25201-2010  5.2条

石小东   回复: 五棱镜中看世界2022-03-21 18:02

放在门卫室,门卫需要取初级消防设施操作员证嘛?

0    0 [回复]举报

天天消防   回复: 石小东2022-05-19 09:48

管消防报警设施的都要持证上岗,有消控室联动设备的要中级以上的操作证,没有的就要最低的初级证

0    0 [回复]举报