消防水泵吸水管路气囊问题

消防水泵吸水管路做成这样,会形成气囊,怎么补救?有没有好的措施。

忙里偷闲 | 2022-06-14 11:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

牛疼 2022-06-14 11:16 00 [回复]举报

压力表侧边接一个放气阀

忙里偷闲   回复: 牛疼2022-06-14 13:17

吸水管路是负压吧?接放气阀能管用?

0    0 [回复]举报

牛疼   回复: 忙里偷闲2022-06-14 17:21

如果不返工,只能先解决吸水管气囊问题;利用放气阀将吸水管气囊中的空气排出后,关闭铜球阀,后期运行时,定时开启铜球阀排气检查。

0    0 [回复]举报

周家斌 2022-06-14 13:51 00 [回复]举报

返工吧,在母管上部开孔,鸭脖弯头解决,规范说明有图例

忙里偷闲   回复: 周家斌2022-06-14 14:24

只有返工一条路吗?


0    0 [回复]举报

阳明心 2023-05-09 10:13 00 [回复]举报

压力表上本来就应该有旋塞的,可以用来排气,算是好的补救办法。