消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

建规图集18j811-1中6-18页图示5中管井门是丙级防火门可以吗?

如图,上图为石峥嵘老师编的书中的说法,按其关于管井防火门等级的说法,图集中的丙级防火门是有误的,请问前室内管井防火门必须是乙级还是丙级?,还是各地要求不同?

wenhua | 2022-10-23 18:39
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

充楞装傻 2022-10-24 10:34 00 [回复]举报

我认为管道井的门上部和下部都是墙体,门在中间部位。

防火封堵和电缆电线的阻燃性能,这里相对是比较安全的。

火灾的蔓延主要是上面的烟扩散和下面的可燃物扩散,中间部位没必要要求那么严苛。


实际应用中丙乙甲都差不几个钱,设计按乙设计不会错。

周家斌 2022-10-24 19:24 00 [回复]举报

按照建规图集执行就可以了,当然提高等级没错,参考就行!

疏散楼梯 2022-11-03 10:21 00 [回复]举报

石老师说的没有问题,如果是单独的电缆井是可以设置丙级防火门,但它处在合用前室,那么就要遵循合用前室的要求,可参考防火规范6.4.3条中的解释

关闭

关闭

手机APP下载