消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

餐饮后厨的成品冷库,外墙是金属面绝热夹芯板,是否需要达到2.0h的防火要求

餐饮后厨的成品冷库,外墙是金属面绝热夹芯板,是否需要达到2.0h的防火要求,有什么规范依据吗

SYL | 2023-05-19 18:15
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

安洪全 2023-05-23 11:02 00 [回复]举报

建筑防火通用规范 GB55037-2022

4.1.3 下列场所应采用防火门、防火窗、耐火极限不低于2.00h的防火隔墙和耐火极限不低于1.00h的楼板与其他区域分隔:    

1 住宅建筑中的汽车库和锅炉房;   

2 除居住建筑中的套内自用厨房可不分隔外,建筑内的厨房;    

3 医疗建筑中的手术室或手术部、产房、重症监护室、贵重精密医疗装备用房、储藏间、实验室、胶片室等;   

4 建筑中的儿童活动场所、老年人照料设施;    

5 除消防水泵房的防火分隔应符合本规范第4.1.7条的规定,消防控制室的防火分隔应符合本规范第4.1.8条的规定外,其他消防设备或器材用房。

关闭

关闭

手机APP下载