防火隔墙可以用石膏板吗?

防火墙和防火隔墙的区别是什么?防火隔墙可以用石膏板吗?

阳明心 | 2023-06-15 09:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-06-15 12:31 10 [回复]举报

2.1.11 防火隔墙 fire partition wall     建筑内防止火灾蔓延至相邻区域且耐火极限不低于规定要求的不燃性墙体。


2.1.12 防火墙 fire wall     防止火灾蔓延至相邻建筑或相邻水平防火分区且耐火极限不低于3.00h的不燃性墙体。


区别:耐火极限不同,使用位置不同,用途也不同。


防火隔墙可以采用石膏板作为材料

同同不同 2023-06-15 13:50 10 [回复]举报

石膏板可用作防火隔墙,可采用纤维石膏板、纸面石膏板、耐火纸面石膏板、防火石膏板等,但应满足隔墙的耐火极限,可参照建规附录做法

超级鹏 2023-06-29 11:13 00 [回复]举报

建筑防火通用规范 GB55037-2022 条文解释6.2.1

防火隔墙主要用于同一防火分区内不同用途或火灾危险性的房间之间的分隔,耐火极限一般低于防火墙的耐火极限要求。防火隔墙要尽量采用不燃性材料且不宜在墙体上设置开口,一、二级耐火等级建筑中的防火隔墙应为不燃性实体结构,木结构建筑和三、四级耐火等级建筑中的防火隔墙允许采用难燃性墙体。