强氧化剂车间(甲乙类)需要设计防爆吗

强氧化剂车间(甲乙类)需要设计防爆吗

刘和 | 2023-07-20 09:49
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

同同不同 2023-07-20 10:22 00 [回复]举报

需要进行防爆、泄爆设计

hnlyplszq 2023-07-20 10:29 00 [回复]举报

强氧化剂属于甲类,容易发生爆炸,需要设计防爆泄压。

安洪全 2023-07-20 10:37 00 [回复]举报

有爆炸危险的场所,需要做防爆设计。

周家斌 2023-07-20 14:30 00 [回复]举报

建筑防火通用规范 GB55037-2022:2.1.7 建筑中有可燃气体、蒸气、粉尘、纤维爆炸危险性的场所或部位,应采取防止形成爆炸条件的措施;