房间分割后的疏散门问题

规范说办公建筑房间面积>120㎡需要两个疏散门,假如办公建筑的一个房间面积200㎡被分割成多个房间,每个房间的面积都<120㎡,那么通往疏散通道设一个门可以吗?不可以又是为什么?

| 2023-10-26 16:16
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

澜沐 2023-11-02 09:58 10 [回复]举报

首先,《通用规》第7.1.2条规定明确房间的疏散门应当直通安全出口,不应经过其他房间。

但考虑二次装修的复杂性,规范没办法一一阐述;按你所说的,一个房间里设置房中房(作为该房间的辅助用房),那么房中房的面积应当计入该房间的整体面积来进行考虑设置疏散门的数量,否则就已经不符合上述的条文。


以上为个人见解。