高层住宅连廊未设置常闭门,导致走道为半敞开空间,走道安装的湿式系统的喷头,在冬天极端天气,气温在零下5度左右,喷头会受影响吗?可以采取什么措施,消除极端天气的影响?请教一下,谢谢啦!

淡雅 | 2024-03-15 12:47
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

消防网友39103 2024-03-16 14:54 00 [回复]举报

伴热管,比较经济合理,毕竟冬天总会过去,也就那么几个月吧。

听雨眠 2024-03-18 08:17 00 [回复]举报

电伴热

钻孔 2024-03-19 01:08 00 [回复]举报

上海地区的做法:采用易熔合金喷头,管道做橡塑保温

麻溜点 2024-03-19 17:11 00 [回复]举报

零下5度肯定会受影响,最简单就是把喷头换成易熔合金喷头。管道做保温。