消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防稳压系统配电需要设置双电源吗?

请问消防稳压系统配电需要设置双电源吗?

| 2024-07-07 15:04
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2024-07-08 09:08 00 [回复]举报

稳压泵也是消防泵的范畴,,作为一级负荷的场所,是需要双电源的,

潘天坤   回复: 周家斌2024-07-08 13:19

周老师,稳压泵是否属于消防水泵可能存在一些争议(消水规GB50974里面关于稳压泵和消防水泵的描述一般都有分开描述,也分为不同章节),不过赞同您的负荷等级观点,一般水泵负荷等级要求会比较高,一般与建筑内最高负荷同等级或者低一级

以上为个人理解,不一定对,如果有说的不对的地方还请周老师指正

0    0 [回复]举报

南明离火 2024-07-08 09:51 00 [回复]举报

依据原建筑,原建筑消防设施有双电源,那么稳压泵也需要

潘天坤 2024-07-08 13:22 00 [回复]举报

可能需要看建筑的最高负荷等级是几级,如果最高负荷等级是三级,那也就没有双电源的说法了(建筑防火通用规范 GB55037-2022第10.1.6条规定:除按照三级负荷供电的消防用电设备外,消防控制室、消防水泵房的消防用电设备及消防电梯等的供电,应在其配电线路的最末一级配电箱内设置自动切换装置,消防水泵都如此要求了,更不用说稳压设施了)

稳压设施的电源一般是与建筑最高负荷同级或者低一个级别(但是如果建筑最高负荷等级为二级,一般也不会低于二级)


关闭

关闭

手机APP下载