消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

床位 50 个以上养老场所使用 5kg 干粉灭火器?

床位 50 个以上养老场所使用 4kg 干粉灭火器多组布置,  采用 5kg 干粉灭火器。

leekeygao | 2024-09-18 09:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

磊中 2024-09-18 09:19 20 [回复]举报

是的,50张床位及以上的属于严重危险级,所以单具灭火器级别应该是3A的所以要用5KG或6KG的干粉灭火器

logical 2024-09-19 10:39 00 [回复]举报

阿龙 2024-09-20 17:16 00 [回复]举报

根据《建筑灭火器配置设计规范》(GB50140-2015)4.1.1 灭火器的选择应考虑下列因素:
1 灭火器配置场所的火灾种类;
2 灭火器配置场所的危险等级;
3 灭火器的灭火效能和通用性;
4 灭火剂对保护物品的污损程度;
5 灭火器设置点的环境温度;
6 使用灭火器人员的体能。

理论上应配置5KG的干粉灭火器,但是还要考虑到养老场所大多数都是体质较弱的老年人和女护工,选择配置小规格的手提式灭火器,也是对本款规定的一种考虑,所以用4KG也可以。

关闭

关闭

手机APP下载