消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

我想问问我理解的消防用水量之和的公式计算是否有误?

如图所示:

澜沐 | 2021-11-26 11:48
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

刘丽波 2021-11-26 16:58 00 [回复]举报

一次火灾用水量只考虑一处着火,在一个防火分区内的各系统用水量,综合计算的最大值。不是各系统用水量最大值的叠加。因为各系统的最大值不一定同时在一个防火分区内。

关闭

关闭

手机APP下载