烟花爆竹专卖店或者专卖点需要办理消防开业前消防安全检查吗

烟花爆竹产品属于甲类还是乙类产品,其经营场所需要办理开业前消防安全检查手续吗,他属于超市类吗。

哟呀 | 2025-02-21 12:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

赖峰 2025-02-22 15:57 00 [回复]举报

答案:烟花爆竹不用甲乙类区分,烟花也不属于公众聚集场,无需办理消防开业前消防安全检查。


烟花爆竹不适应《建筑设计防火规范》 GB50016-2014(2018年版)的3.1 火灾危险性分类
参考:建筑设计防火规范 GB50016-2014(2018年版) 1.0.3 本规范不适用于火药、炸药及其制品厂房(仓库)、花炮厂房(仓库)的建筑防火设计。


另《中华人民共和国消防法》第十五条规定。公众聚集场所投入使用、营业前消防安全检查实行告知承诺管理。其中公众聚集场未提及烟花这样的场所。